DonW
R.I.P.
I'm doing this one for my life long friend that has freshwater planted aquariums. There are two tanks but no sump. The tanks are connected together, so one tank flows into the other. This will work fine on sumpless reefs also.
What we know:
The water level is 1" from the top on both tanks when full.
There is a large amount of surface agitation due to the way they overflow.
Water level can not fall more than 1" or it effects the over flow.
Madison ms8000 float switch activates at 3/4" of fresh water 5/8 for SW.
The ato pump will flood the tanks in 14 minutes after the water level is at its intended level.
With the level being so high we cant use a back-up float switch.
There is only 1/16" hysteris in the Madison ms 8000 float switch.
The is usually (not in this case) a challenge and requires some expensive electronics to be safe. I think part of the reason we dont see alot of sumpless ato systems.
Parts:
1 Plastic box
1 Madison ms8000 float switch
1 Reef Werks universal Module
1 12vdc wall transformer aka wallwart
Msc crimp connectors
In this case the ato pump is a tunze osmosilator low voltage pump.
First step is the Universal module. We know the hysteris is way to small so we need to add hysteris. We know that the pump should not be allowed to top off for more than 14 minutes.
The module is programmed when when ordered and is flashed into the memory so it stays there until it gets flashed again.
Add 30 minute delay after float switch activates this will give a little extra time for the level to stabilize and wont hammer the pump on and off.
Add 14 minute failsafe so that the ato pump cant flood the tank if the float were to fail.
We'll throw in a 2 hour period that the system cant do anything after the fail safe. This is just in case and sound good to me.
More Later
Don
What we know:
The water level is 1" from the top on both tanks when full.
There is a large amount of surface agitation due to the way they overflow.
Water level can not fall more than 1" or it effects the over flow.
Madison ms8000 float switch activates at 3/4" of fresh water 5/8 for SW.
The ato pump will flood the tanks in 14 minutes after the water level is at its intended level.
With the level being so high we cant use a back-up float switch.
There is only 1/16" hysteris in the Madison ms 8000 float switch.
The is usually (not in this case) a challenge and requires some expensive electronics to be safe. I think part of the reason we dont see alot of sumpless ato systems.
Parts:
1 Plastic box
1 Madison ms8000 float switch
1 Reef Werks universal Module
1 12vdc wall transformer aka wallwart
Msc crimp connectors
In this case the ato pump is a tunze osmosilator low voltage pump.
First step is the Universal module. We know the hysteris is way to small so we need to add hysteris. We know that the pump should not be allowed to top off for more than 14 minutes.
The module is programmed when when ordered and is flashed into the memory so it stays there until it gets flashed again.
Add 30 minute delay after float switch activates this will give a little extra time for the level to stabilize and wont hammer the pump on and off.
Add 14 minute failsafe so that the ato pump cant flood the tank if the float were to fail.
We'll throw in a 2 hour period that the system cant do anything after the fail safe. This is just in case and sound good to me.
More Later
Don